Hello all. I'm running #3 thhn for a 125 amp pool sub panel. I was wondering if I could run #6 thhn for the ground and nuetral wires. Its a 90' run in underground electrical epvc.
 
I can not (ethically) answer your question because #3, even copper, is not large enough for a 125 amp feeder.
 
  • Like
Reactions: MTW
You need to make the overcurrent protective device 100 amps assuming 75C. A number 6 would be fine for both the neutral and equipment grounding conductor if the load doesn't require more.
 
Hello all. I'm running #3 thhn for a 125 amp pool sub panel. I was wondering if I could run #6 thhn for the ground and nuetral wires. Its a 90' run in underground electrical epvc.
Do you mean the sub panel is rated for 125 amps?
As Dennis said, the answer depends on the OPD
 