Hello all. I'm running #3 thhn for a 125 amp pool sub panel. I was wondering if I could run #6 thhn for the ground and nuetral wires. Its a 90' run in underground electrical epvc.
Do you mean the sub panel is rated for 125 amps?Hello all. I'm running #3 thhn for a 125 amp pool sub panel. I was wondering if I could run #6 thhn for the ground and nuetral wires. Its a 90' run in underground electrical epvc.
That is the question, I’ve fed 125s with a 60 amp feeder.Do you mean the sub panel is rated for 125 amps?
As Dennis said, the answer depends on the OPD
T250.66 is not applicable for an EGC.NEC T. 310.16/ T. 250.66
I can not (ethically) answer your question because #3, even copper, is not large enough for a 125 amp feeder.
Yes the sub panel is rated for 125 amps.Do you mean the sub panel is rated for 125 amps?
As Dennis said, the answer depends on the OPD
the panel can be 125 A bus as long as the feeder is protected by something rated to protect the #3 copper.I can not (ethically) answer your question because #3, even copper, is not large enough for a 125 amp feeder.