Perhaps someone can help me by explaining about (or) the remedy for ground overcurrent for a Power Distribution Unit (PDU). My past experience in this type of problem was as follows: With single phase circuits the amperage load returning on the neutral conductor must match the same amperage on the hot phase conductor, or there is a leakage to ground causing a Ground Overcurrent situation. This can cause an alarm on monitoring equipment when the preset load is reached. Thus the problem I am identifying/repairing in following the work performed by others.
The PDU is a Separately Derived System with a 480 volt Delta and a 120/208 volt Wye Step Down Transformer, having three 225 ampere-42 circuit loadcenters. The PDU itself is used for Data eqipment within the area. The PDU has a system monitor for Voltage, Amperage, KW, Ground Overcurrent, etc. The alarm threshold for Ground Overcurrent is set at 5 amperes and currently the Ground Overcurrent displayed is 9.4 ampere. When a ampere reading is taken on the Grounded or Neutral Bussbar, which contains the grounding electrodes and the grounded conductor bonding point the reading is 8.9 ampere. From one of the PDU loadcenters there is a 100 ampere breaker feeding a 3 phase-4 wire with ground 120/208 volt sub-panel, using 2 AWG-CU THHN conductors with a distance of about 100 feet. The amperage is as follows: A phase-15.9, B phase-20.0, C phase-8.9, and the Neutral is 32.8. On the grounding conductor there is a ground overcurrent of 4.1 ampere, returning back to the PDU. This sub-panel has branch breakers which supply single phase 110 volt duplex receptacles, using 10/2 MC cable as the wiring method. The utilization equipment for the loads are Flat Screen LCD Televisions, which use a two wire male cord connector (no grounding conductor). The televisions have a power supply which reduces the supply voltage from 110 VAC to 13.5 volt DC and the load on each LCD television is 0.5 ampere.
When reading amperage on each brach circuit grounding conductor supplied by the Sub-panel there is Ground Overcurrent present. It appears that as more LCD Televisions are installed on each circuit, the Ground Overcurrent increases. When the grounding conductor is lifted from the Equipment Grounding Bar of the Sub-panel, there is little or no change of Ground Overcurrent readings at the PDU Loadcenter Monitor. I contacted the manafacture of the LCD Televisions and was advised that this Ground Overcurrent is not the fault of the manafactures product being used.
Could this Ground Overcurrent be caused by "Harmonics on the Neutral(s)" of the circuits? Could this be caused by "Inductance" of the MC cables in close proximity of a higher voltage of 277/480 volts AC? Could there be other Grounding issues not addressed upon the initial installation process? Other than identifying each problem circuit cable and tracing each Ground Overcurrent to achieve a zero ampere reading, does anyone have a suggestion how to approach this problem?
Thank you for your help.
RMF
The PDU is a Separately Derived System with a 480 volt Delta and a 120/208 volt Wye Step Down Transformer, having three 225 ampere-42 circuit loadcenters. The PDU itself is used for Data eqipment within the area. The PDU has a system monitor for Voltage, Amperage, KW, Ground Overcurrent, etc. The alarm threshold for Ground Overcurrent is set at 5 amperes and currently the Ground Overcurrent displayed is 9.4 ampere. When a ampere reading is taken on the Grounded or Neutral Bussbar, which contains the grounding electrodes and the grounded conductor bonding point the reading is 8.9 ampere. From one of the PDU loadcenters there is a 100 ampere breaker feeding a 3 phase-4 wire with ground 120/208 volt sub-panel, using 2 AWG-CU THHN conductors with a distance of about 100 feet. The amperage is as follows: A phase-15.9, B phase-20.0, C phase-8.9, and the Neutral is 32.8. On the grounding conductor there is a ground overcurrent of 4.1 ampere, returning back to the PDU. This sub-panel has branch breakers which supply single phase 110 volt duplex receptacles, using 10/2 MC cable as the wiring method. The utilization equipment for the loads are Flat Screen LCD Televisions, which use a two wire male cord connector (no grounding conductor). The televisions have a power supply which reduces the supply voltage from 110 VAC to 13.5 volt DC and the load on each LCD television is 0.5 ampere.
When reading amperage on each brach circuit grounding conductor supplied by the Sub-panel there is Ground Overcurrent present. It appears that as more LCD Televisions are installed on each circuit, the Ground Overcurrent increases. When the grounding conductor is lifted from the Equipment Grounding Bar of the Sub-panel, there is little or no change of Ground Overcurrent readings at the PDU Loadcenter Monitor. I contacted the manafacture of the LCD Televisions and was advised that this Ground Overcurrent is not the fault of the manafactures product being used.
Could this Ground Overcurrent be caused by "Harmonics on the Neutral(s)" of the circuits? Could this be caused by "Inductance" of the MC cables in close proximity of a higher voltage of 277/480 volts AC? Could there be other Grounding issues not addressed upon the initial installation process? Other than identifying each problem circuit cable and tracing each Ground Overcurrent to achieve a zero ampere reading, does anyone have a suggestion how to approach this problem?