Is it legal to run your grounding conductor in a seperate pipe than the ungrounded conductors?
crossman said:Assuming you are talking about branch circuits or feeders and equipment grounding conductors:
2008 NEC
300.3(B) is the general section that says "they must be in the same raceway with the circuit conductors."
300.3(B)(2) allows it for existing installations as per 250.130(C). This may be used when replacing existing 2-wire receptacles with 3 wire receptacles. Also, Equipment Bonding Jumpers may be on the outside of a raceway.
As for circuits in one counduit, EGC in another, the answer is pretty much "no".
duluthelectrical said:There is 600's in the 390' rigid run
The problem with running a single ground in a metalic pipe is when a fault tries to carry down the conductor the pipe acts as a choke and builds magnetic resistance as the amperage increases sudenly.crossman said:Okay, let us assume it is rigid metal conduit.
Now, 250-118 says RMC is approved as an EGC. So, we actually don't even need an EGC wire in the pipe. So.... if we, just for fun, wanted to run a conduit from the inverter to the other piece of equipment, and we wanted to pull a single 3/0 in it, and tie it to the Equipment Ground at each piece of equipment, would there be an issue then?
As far as I know, there is nothing preventing us from bonding equipment together just for the "fun" of it. We can put bonding jumpers wherever. And we can protect them from physical damage by placing them in conduit?
So, maybe that is the way to get around this.
quogueelectric said:The problem with running a single ground in a metalic pipe is when a fault tries to carry down the conductor the pipe acts as a choke and builds magnetic resistance as the amperage increases sudenly.
It would not be a code issue, but would they serve any real purpose?crossman said:The Code is a minimum. If I want to run copper bonding jumpers all over the place in my building, connecting all my equipment together, I don't think the Code stops me.
It is still a violation if the boss calls it an EGC:grin:crossman said:But I was referring to the OP. If the existing feeder is in RMC and the boss wants to run a second conduit and install a 3/0 conductor in it and attach it to the equipment, I don't see that there is a code violation.
don_resqcapt19 said:It is still a violation if the boss calls it an EGC:grin: