Re: Ground resistance for conduit/box connections
Let me make a comment on checking boxes, conduit, etc. for continuity of ohms resistance.
I worked for the DuPont Co. at the Chambers Works site, Deepwater, N.J. for 45 years.
DuPont had a procedure called "Fault & Static Inspection". This meant that we were to check every stick of conduit from the ECR to the device, being a solenoid valve or a motor, also building steel with a ohmmeter. We were to see zero ohms to ground. For example, if we came to a stick of conduit and at the coupling that may have corroded, and on one side we would see zero ohms, but on the other side, we would see a higher reading of ohms. We would install a jumper wire to correct the situation.
I might add, back a few years ago, we would relie on the conduit for our ground continuity, back to the source. Today, they still have the conduit continuity, but they install a ground wire internally in the conduit. I totally agree with installing the ground wire inside of the conduit.