Ground Resistance Testing
Could someone help me with procedures for testing the ground resistance with a clamp on meter. I have a 3/0 copper conductor from the service neutral to (2) 10' rods and to the building steel. Where would be the best place to clamp for an accurate reading?
Is this a clamp-on ground-resistance tester, or merely a clamp-on ammeter?
If the former, read the instructions; if the latter, you really can't.
Mike:
Where are you trying to read the resistance with this clamp. (I assume it is designed for this purpose.
We use the AEMC tester the best thing I could recommend is reading this site.
You have to be careful utilizing this meter, many companies I have done work for use these clamp on testers and the way they utilize them is improper for the application.
http://www.aemc.com/techinfo/appnotes/Ground_Resistance_Testers/APP_3711_3731_Useage.pdf
Larry have you read the instructions for this type of meter, I have and are not very clear. I am familiar with series and parallel risistance formulas. But I have not used this meter before. When I clamp on G.E.C I get a reading of
.037 ohms. If I disconnect from the neutral I get 999 ohms
dereckbc said:
You were reading a loop, common mistake.
The number of test reports I have seen with this result. The reason see the reports as our follow or retest after several years does not match the original test.