Ground Resistance

Status
Not open for further replies.

timm333

Senior Member
Location
Minneapolis, MN
Occupation
Electrical Design Engineer
We measure the ground-resistance of rod-electrodes using three point method. How do we measure the ground resistance in the case of a ground-ring? Also when we say that the ground resistance is 10 ohm, what does it actually mean; the definition is that the ground resistance is the resistance between the electrode and remote earth, what does remote earth mean here? Thanks
 
We measure the ground-resistance of rod-electrodes using three point method. How do we measure the ground resistance in the case of a ground-ring? Also when we say that the ground resistance is 10 ohm, what does it actually mean; the definition is that the ground resistance is the resistance between the electrode and remote earth, what does remote earth mean here? Thanks

With a single rod, ring, Ufer ground grid or any grounding configuration you can use the 3 point method. Just make sure that the 2 test rods are "out of the sphere of influence" to be an accurate measurement. This means connect one test lead to any point in the system (preferably a corner) then drive the 2 test rods outside and away from the ground system. The length of the other 2 test leads will determine the distance of the rods. If I remember correctly, with the Biddle test set, the distances are: Test point = 0 ft., 1st Test Rod = 65 ft, 2nd Test Rod = 100ft (all outside the ground system.)
If you think of the earth (remote earth) as the perfect ground then its resistance
would be 0 ohms ( or the smallest value you can imagine, micro-ohm, nano-ohm, etc.) So this ground resistance value measured is the resistance between the ground system (or electrode) and the perfect earth. Hope this makes sense.
 
Yes I think I understand now: the resistance is more in the vicinity of electrode, and as the distance increases, the resistance decreases until a point where the resistance becomes almost zero, this point is called remote earth.

So if we use a ground ring conductor placed about 3 feet away around the outer perimeter of the steel structure: will it be enough, or will we still need to use the concrete encased rebar (below the structure) as part of ground electrode in order to reduce the potential rise?
 
Just be aware that for a large distributed GES the sphere of influence can be very large. Larger than the 65 and 100 foot lead lengths.
And there cannot be other GES systems beyond the one under test which whose sphere of influence also overlaps the test electrodes.
In particular, for a ring ground the critical dimension is not the depth of the electrode, it is the length of that side of the building.
For an indefinitely long horizontal line electrode the potential falls off inversely to the distance rather than inversely to the square of the distance.

Hence Atsman's advice to move out from a corner if possible.
 
Why does the ground grid of substation has to be different than the ground grid of other structures?

To explain Goldigger's reply in laymans terms: the GES system of substations is much more stringent than residential, commercial and industrial applications due to the fact of the much higher concentration of magnetic and electrostatic fields present in these areas of MV and HV transformers, power lines, etc. It all has to do with personnel safety working in these different environments. You have probably seen the chain link fences at these subs tied to ground rods every 10 ft or so just to bring the touch potential as low to ground as possible to reduce shock hazard. Hope this explains it some as I'm not sure I explained it very well.
 
Why does the ground grid of substation has to be different than the ground grid of other structures?

To add, you also want to minimize ground potential gradients. Without proper grounding, a ground fault in a substation can generate a steep enough potential gradient to produce lethal voltage between the distance of a person's step.
 
To explain Goldigger's reply in laymans terms: the GES system of substations is much more stringent than residential, commercial and industrial applications due to the fact of the much higher concentration of magnetic and electrostatic fields present in these areas of MV and HV transformers, power lines, etc. It all has to do with personnel safety working in these different environments. You have probably seen the chain link fences at these subs tied to ground rods every 10 ft or so just to bring the touch potential as low to ground as possible to reduce shock hazard. Hope this explains it some as I'm not sure I explained it very well.

The reason for the beefier GES in a substation is simply due to fault current. The same touch potential still has to be maintained so, you have to provide more paths for the fault current during a fault to achieve safe potentials.
 
I don't think that the GES is near as important as the equipotential grid in maintaining safe step and touch potentials in a substation under fault conditions. The grid makes sure everything rises to the same potential above remote earth. This voltage above remote earth can be thousands of volts above remote earth, but if everything is at the same potential there is no step or touch hazard even though the voltage to remote earth is very high.
 
I don't think that the GES is near as important as the equipotential grid in maintaining safe step and touch potentials in a substation under fault conditions. The grid makes sure everything rises to the same potential above remote earth. This voltage above remote earth can be thousands of volts above remote earth, but if everything is at the same potential there is no step or touch hazard even though the voltage to remote earth is very high.

Not sure I agree. Logic suggests that as the system voltage increases then the integrity (beefiness) of the
GES is directly proportional with regard to personnel safety.
 
The reason for the beefier GES in a substation is simply due to fault current. The same touch potential still has to be maintained so, you have to provide more paths for the fault current during a fault to achieve safe potentials.

I think you are mixing 2 separate issues. Fault current and the interruption of it has
nothing to do with personnel safety. You are talking about protection devices that limit
the fault current with milliamps that can kill someone. :happysad:
 
Not sure I agree. Logic suggests that as the system voltage increases then the integrity (beefiness) of the
GES is directly proportional with regard to personnel safety.
I don't see the GES, the connection to earth, as reducing the step or touch potential. I see the equipotential grid as doing that. That is everything including the equipotential grid is at the same voltage...a voltage that will be much above the voltage of the earth under fault conditions.

That being said, since the connection to the earth is part of the fault clearing path for utility circuits, the better the connection to earth, the more current that will flow and the quicker the fault will be cleared. When the fault is cleared the step and touch potentials go away. This also means that the equipotential grid has to take voltage drop across the grid into account to limit the step and touch potentials.
 
I don't see the GES, the connection to earth, as reducing the step or touch potential. I see the equipotential grid as doing that. That is everything including the equipotential grid is at the same voltage...a voltage that will be much above the voltage of the earth under fault conditions.

That being said, since the connection to the earth is part of the fault clearing path for utility circuits, the better the connection to earth, the more current that will flow and the quicker the fault will be cleared. When the fault is cleared the step and touch potentials go away. This also means that the equipotential grid has to take voltage drop across the grid into account to limit the step and touch potentials.

Don and Mivey,
I stand corrected.....must of had too much vino when I wrote that....:slaphead:
I did some reading and found this:
http://donaldwzipse.com/images/PID642277.pdf
 
Heres something I typed up a month ago, but I think its well worth it in this thread:


Here is the irony: In the EU and other parts of the world the term earth simply means the exact same thing as ground to us: an all encompassing term for everything in article 250. Earth not only means soil, but EGC, bond, and a list of other things which most of them have nothing to do with soil.

The truth is both our term ''ground'' and the European Unions term ''Earth'' is incorrect. In fact IMO the only ones who have the term right is Canada which refers to EGCs as bond wires. Fault clearing and equal potential the heart of electrical safety and the ultimate intention of article 250 have everything to do with bonding with little to do in the way of earthing.

Basically it boils down to two parts:

A. Equal potential based on a faraday cage design: which is connecting (bonding) all metallic parts that could become energized together with a large enough conductor.

B. Bonding jumper. If the first part is successful this part is theoretically optional, but still needed most of the time: Connecting (bonding) the equal potential (faraday cage) to the source with a sufficiently sized conductor. The primary purpose is to intentionally allow a place for current on the equal potential system to go during a fault thus immediately tripping a breaker.

Both parts relay entirely on bonding.

The ground rod is really only for lightning discharge, which helps to lessen the damage.

Yes grounds rod dissipate a lightening strike, and they do in a few occurrences, but they do nothing for human safety. Even when a high voltage primary crosses over into a secondary, yes a ground rod provides another path for that current, and they may help in such a case, but what really protects people and property is bonding.


Consider these 2 examples; both identical buildings with a concrete rebar enforced slab foundation and wood framing. In many buildings there is a huge flaw from the start, that being no ufer bonding takes place. Building 1 has no UFER and thus ground rods are driven, while building 2 has a UFER bond but no ground rods. Both water lines are plastic going into the structure but transition to metal in the building. No gas exists but an AHU inadvertently bonds the duct work to the metal frame with an EGC.

Here is what happens during an open neutral. Both example hold true with a 120, 230 and 277 ect volt service. When the neutral opens the ground system will become energized by what ever the difference is between the 120 or 277 volt loads relative to remote earth. Under the voltage imbalance something may overheat and short circuit hot to neutral putting 120 or 277 volts on the bonding system. In a 230 volt single phase feed the potential will be 230 volts since the neutral is not shared. For the sake of the argument lets say the bonding system is 120 volts to remote earth. The key here is human safety:

1. In building #1 all appliances relative to each other will read zero volts. Contacting a fridge and an oven will give no dangerous potential. Washer to dryer no potential. Even metal plumbing, such as a sink to a light switch no potential. Plumbing to duct work, no potential. Nothing will be dangerous relative to one another. An exception is an outdoor water spigot that will read 120 volts to earth. If that reading was taken within inches of the ground rods potential will be perhaps less than 120 volts (say 60 volts), but go beyond a few inches it will be close to 120 volts. Soil resistance dictates how low the voltage will be around the ground, but regardless of soil conditions, go past a foot or two at best and the ground rod will no longer give equal potential. I could drive more ground rods, but it would change nothing. Id be safest literally standing on a ground rod (zero volts) while contacting the water spigot, but beyond that I have no protection. Nor do I get a second neutral for my loads.


One would think the person inside is safe, since they are not in contact with soil. FALSE. Like most buildings the UFER was left out of the picture. The potential between a sink and the bathroom floor will be 120 volts. Between duct work and the floor 120. Bonded Drill and floor 120. This voltage potential only exists from the lack of bonding, even though the UFER is the ultimate ground rod. If a person took off their shoes and touched the electrical panel cover or anything else metal, the probability of electrocution is there.



2. Now in building #2 the Ufer is bonded. When the neutral opens, being barefoot will not expose the person to dangerous step touch potential. I could be wet, barefoot and touching the furnace, stove, electrical panel... because the UFER is bonded I will not be in any danger. Even if the UFER's resistance to soil is to high to be a good neutral bath back to the source, or even if its close to zero ohms, it does not matter since bonding will maintain that equal potential regardless what happens. I can go further in that equal potential not only protects people it eliminates fire hazards. A difference in potential can cause immense current to flow unrestrained on something that might not be able to carry it.


That same concept also hold true for incidental contact with higher voltages. Its not so much the grounding, but the bonding that protects people and property. With that said places with out a UFER are no different that places with unbounded plumbing, yet AHJ make the wrong assumption one is dangerous the other is not.
 
...
The truth is both our term ''ground'' and the European Unions term ''Earth'' is incorrect. In fact IMO the only ones who have the term right is Canada which refers to EGCs as bond wires. Fault clearing and equal potential the heart of electrical safety and the ultimate intention of article 250 have everything to do with bonding with little to do in the way of earthing. ...
There are public inputs to make this change for the 2017 NEC....maybe CMP5 will listen this time!
 