I am designing a low-resistance grounded system for a double-ended substation. How to pick the grounding resistor for 50MVA D/Y 120KV-13.2KV transformer 7.74% impedance?
My calculations:
50*1000/sqrt(3)/13.2 = 2200A, pick 10% = 220A; R = 13.2*1000/sqrt(3)/220 = 34 ohm. This gives 440A from the two transformers.
How does the charging current come into play? How does the CT ratio come into play?
My calculations:
50*1000/sqrt(3)/13.2 = 2200A, pick 10% = 220A; R = 13.2*1000/sqrt(3)/220 = 34 ohm. This gives 440A from the two transformers.
How does the charging current come into play? How does the CT ratio come into play?