bphgravity said:If 18 is good enough for lightning protection, it should also be good enough for a grounding electrode for a service.
georgestolz said:My only thought is maybe Rob is onto the reason - an NEC grounding electrode would be more strictly protected (by burial depth) than an optional grounding system...right?
And I was offering only uneducated affirmation of your guess.infinity said:I was just taking an edjucated guess.
A ground ring can protect against touch voltages to a grounded building in the event that a primary fault on the utility system causes a high Ground Potential Rise (GPR) on the common primary/secondary ground. A ground fault at the primary of a service transformer can cause a very high GPR and depends a lot on how much current flows back to the substation source through the neutral and how much through the earth.bphgravity said:A ground ring is always an optional grounding method. When used under the NEC, it serves no real purpose. When used under the NFPA 780, it is expected to carry the full surge current of a direct lightning strike.
Which one do you think needs to be more restrictive?