Ground Ring connected to building steel functioning as the telecom bonding backbone?
mcolosimo
New member
Columbus, Ohio
I'm working with a customer who believes that the ground ring installed around the building and connects to the building steel will eliminate the need for a TBB (Telecom Bonding Backbone) to be installed. They simply want to install a TGB in the IDF with a #6awg attached to building steel (column).
Looking for input to convince them that the ground ring does not replace the need to install a separate bonding system for the telecom system.
Thanks in advance!
Mike
Is a separate bonding system that you've mentioned a TIA or some other requirement? I know of no such requirement in the NEC. We connect the telecom grounding system to the building GES.
Welcome to the Forum. :)
Thanks in advance!
Mike
I agree with infinity. Under the NEC there is no such thing as a separate telecom bonding system, everything gets bonded together.
Grounding & Bonding
Grounding & Bonding
Perhaps this TIA may be what Infinity mentions above: Bicsi
https://www.bicsi.org/uploadedFiles/PDFs/Conferences/India/07-Panduit final Preso - OK.pdf
Some facilities may require a certified Communication designer appropriate to provide the development installation.
And under current Code, the connection must be to the intersystem bonding termination (IBT) for new construction. See 250.94, especially the Exception thereto if dealing with an existing building.
I was going to also link the wire sizing table, but it is already in the document NEC_addicted linked to. Refer to page 6 in his document, which increases the wire size based on the distance.
I also agree with the intersystem connection. My understanding is that you want to make sure that the grounds at the receptacles are at the same potential as the telecom grounding system to minimize stray signals/static on the equipment.
I've had equipment destroyed because of a 50 volt difference in potential between the receptacle ground prong and the building steel that the equipment was grounded to.
-Hal
everthing has to bonded together unless isolated i thought... but even that ends up at the main bond anyway or am i missing something
Thanks in advance!
Mike