When designing a Lightning Protection System for a building, when is a ground ring electrode required around the building? What code or standard is this defined in? Thanks in advance for your responses.
When designing a Lightning Protection System for a building, when is a ground ring electrode required around the building? What code or standard is this defined in? Thanks in advance for your responses.
I am not a LP expert but I do not think that 780 ever "requires" a ground ring as long as all the down leads are terminated at an acceptable grounding electrode. It is a design decision.
The UFC requires counterpoise (ground ring) on many government projects.