Ground ring or not

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have three ground rods 8 feet apart connected by one continuous 24 feet long minimum #2 awg copper in a circle but does not encircle the building. Would this be ground ring or just ground rods?
 
I have three ground rods 8 feet apart connected by one continuous 24 feet long minimum #2 awg copper in a circle but does not encircle the building. Would this be ground ring or just ground rods?
It is not a ring if it doesn't encircle the structure.

What you have is often called a Triad when the 3 rods are in a triangle.
 
I agree not a ground ring just a ground rod electrode. Question is why does it matter?
 