We have a water reservoir, being constructed of reinforced concrete. It is approximately 400' x 200' in size. A subconsultant performed the electrical design.
No electrical equipment and no electric service is present at this structure.
The original design did not include grounding (ground rods) for the structure. The reservoir is now under construction. The subconsultant has had a change of electrical staff, and the new electrical engineer feels that grounding IS required. They are proposing a ground ring around the reservoir, bonded to the rebar in the concrete.
Based on the below comments - from another thread - I am uncertain if the grounding is required.
Does this structure require grounding? If so, please generally describe what is required.
Thank you.
Refer to this thread where the following statement was agreed upon:
"If the water pipe, the structural steel and/or the concrete encased electrodes are present, there is no need for ground rods to be installed.":
http://forums.mikeholt.com/showthre...?highlight=concrete+ground+without+electrical
No electrical equipment and no electric service is present at this structure.
The original design did not include grounding (ground rods) for the structure. The reservoir is now under construction. The subconsultant has had a change of electrical staff, and the new electrical engineer feels that grounding IS required. They are proposing a ground ring around the reservoir, bonded to the rebar in the concrete.
Based on the below comments - from another thread - I am uncertain if the grounding is required.
Does this structure require grounding? If so, please generally describe what is required.
Thank you.
Refer to this thread where the following statement was agreed upon:
"If the water pipe, the structural steel and/or the concrete encased electrodes are present, there is no need for ground rods to be installed.":