In substations where I do most of my work, parallel and multiple ground paths in current transformer ckts. that are connected to protective relays are a scourge. Recently, while I was working on control wiring problem in a substation, a 13 kv feeder that originated in this same sub experienced a hard ground fault. Because the neutral conductors in several ct ckts had been connected to earth ground in multilple locations, a portion of the ground fault return current appeared in the neutrals of these ct circuits.(these neutrals were in effect "in parallel" with the grounding grid) This resulted in a breaker failure relay operation at the 161kv level which dumped part of a large substation. Half of the 13 kv switchgear was also lost due to a differential operation which caused loss of auxilliary operations in a nearby power plant. Two units were taken off line as well as the plant itself going partially dark. In the resulting scramble to find out just what happened, one plant electrician was injured in a fall. All of this from one or two "mis-applied" grounding jumpers.
Another incident involving Pt's and a metering circuit resulted in some damaged digital revenue metering equipment.
Most all literature dealing with protective relays, metering equipment, communications gear warn against multiple and parallel earth connections.
Also, in the electricians or wireman's world, doesn't the NEC mandate that there will only be 1 earth ground connected in a main panel entrance? (I'm not an electrician so my code knowledge is very limited)
I can go on about a substation tech friend of mine who was working on a corner grounded delta secondary and found out the hard way that it was grounded in more than one location(same corner of the delta, different earth ground jumper).
Then there was the flash fried aluminum relay rack that turned out to be in series with a large paralleled run of 4/0 ground grid conductor that turned out to be a favored path of return current for a 69-13 kv 30 MVA power transfomer. The run of 4/0 turned out to be one of only two surving runs left to the X0 bushing after some digging was done in the area.
Then, there was the time...........................
Okay, I'm getting carried away. However, parallel grounding paths placed in the wrong places can cause all kinds of problems and end up getting un-suspecting workers injured. Unfortunately, I've seen it. If you require any more proof of this, I'll be glad to converse with via email. Let me know.