Ground rod 6' apart

Status
Not open for further replies.

SAP

Senior Member
Location
Fresno Ca
My ground rods are 6' apart .I measured along wall 5' along one wall then I hit the corner to transition to the other wall which I go 1' so basically it's like a L figure if I measure diagonal from one ground to other ground rod I'm only at 4.5 feet. I'm I good has long has I have 6' apart along wall thanks
 
Um, no you're not. You don't measure 'along the wall'. You measure 'as the crow flies'. Fault current doesn't have a propensity to flow along the wall.
 
To add to 480's post, the rods should actually be their length apart at minimum.

Roger
 
2011 NEC

250-53(a)(3)

(3) Supplemental Electrode. If multiple rod, pipe, or plate
electrodes are installed to meet the requirements of this section,
they shall not be less than 1.8 m (6 ft) apart.


Informational Note: The paralleling efficiency of rods is increased
by spacing them twice the length of the longest rod.
 
2011 NEC

250-53(a)(3)

(3) Supplemental Electrode. If multiple rod, pipe, or plate
electrodes are installed to meet the requirements of this section,
they shall not be less than 1.8 m (6 ft) apart.


Informational Note: The paralleling efficiency of rods is increased
by spacing them twice the length of the longest rod.

I have always found this IN to be rather dumb, why have a 6' requirement then tell us that 8' or 10' would better?
 