On this service there is no water main electrode.
I have two rods driven through the basement wall, horizontal, at about 6' below grade. The wall is 12" to 14" thick and the rods are counter sunk in about 1 1/2". ( I intend to cover these with concrete patch ) These rods are 8' long. The inspector gave me a correction on this based on that they are not a full 8' into the soil. I contend that code allows for concrete encased electrodes, therefore must recognize the hydrating thus conductive value of concrete. So I see no problem. This seems so petty to me.
What would be you're call??
Thanks
I have two rods driven through the basement wall, horizontal, at about 6' below grade. The wall is 12" to 14" thick and the rods are counter sunk in about 1 1/2". ( I intend to cover these with concrete patch ) These rods are 8' long. The inspector gave me a correction on this based on that they are not a full 8' into the soil. I contend that code allows for concrete encased electrodes, therefore must recognize the hydrating thus conductive value of concrete. So I see no problem. This seems so petty to me.
What would be you're call??
Thanks