It is important to understand equipment grounding enables ground fault protection and grounding to earth does not.
I also receive newsletters from Mike Holt Enterprises and I have one from today ?Grounding Myth No. 2?. This newsletter ended with an obvious reminder of ohms law I = E/R. If the ground rod is relied on for a ground fault path notice this example of a 20A 120V circuit that shorts 50? out: (ground rod resistance at 20 ohms) 6A=120V/20ohms, wow not even a 15A breaker will open! This ground is simply a drain and provides NO protection for ground fault.
But this same example using an equipment grounding conductor: 1200A=120V/.1 (table 9), this breakers going to open instantaneously! Ground rods do not create a safer system for shorting or ground faults although they can provide a route for over-voltages like lightning and such.