I am having a disagreement with a client over the question of whether a metal light pole needs to have a nearby ground rod with a wire connecting the rod to the pole. I surmise that he is concerned over the possibility of a short from the ungrounded conductor to the pole itself, with a person leaning against the pole at the time. I tried to explain that that was the purpose of the EGC, and that (in the absence of an EGC) creating a path into planet Earth would not make the pole safe to touch. I would like to have a code reference handy, for the next time we discuss the issue, as a means of backing up my point of view.
Here is what I take from the NEC:
Here is what I take from the NEC:
- The light pole is a ?structure,? in the context of the article 100 definition.
- The light pole does not need a local disconnecting means, because of Exception 3 to 225.32.
- The light pole does not need a ground rod, because of the Exception to 250.32(A).