I do agree with what your saying but If the intent is not to require the bonding conductor to be connected to the EGC then why is it a requirment in 680.26(B)(4)?By Charlie: That is sort of right. You don't run a #14 in this case to the #8 but you do bond the #8 to the enclosure. It is basically semantics but you don't run the small circuit conductor to the #8.
Where a double-insulated water-pump motor is installed under the provisions of this rule, a solid 8 AWG copper conductor that is of sufficient length to make a bonding connection to a replacement motor shall be extended from the bonding grid to an accessible point in the motor vicinity. Where there is no connection between the swimming pool bonding grid and the equipment grounding system for the premises, this bonding conductor shall be connected to the equipment grounding conductor of the motor circuit .
Where there is no connection between the swimming pool bonding grid and the equipment grounding system for the premises , this bonding conductor shall be connected to the equipment grounding conductor of the motor circuit .
Originally posted by ryan_618:
I'm not saying I agree with this, and I'm not saying I like it...I'm just saying what it says.![]()
I just don't like it in every circumstance. I was talking to one of the moderators about this just the other day, in fact. I like the definition, generally speaking, I just think it can get taken too far.Originally posted by georgestolz:
Ryan, are you saying you don't like the definition in general, or just in this circumstance?
I have thought about "structure", and it seems pretty solid to me.[/QB]
Ryan,I just don't like it in every circumstance. I was talking to one of the moderators about this just the other day, in fact. I like the definition, generally speaking, I just think it can get taken too far