We are installing a three phase Wye Wye step down transformer (480/277 to 208/120), fed from a 480/277 breaker panel. We have a ground rod, UFER and water piping bonds installed for the building 3P4W grounded main service. Do we need to drive another ground rod for the neutral of the step down transformer or can we just connect to the grounding electrodes of the main service? The transformer will feed a three phase 208/120 breaker panel. The high and low side neutrals will not be connected to each other. I assume this makes it a SDS. All equipment is in the same building.
Do I need to run the 480V neutral to the transformer primary neutral if all the breaker feeds is the transformer?