when sizing the GEC for a stand alone generator with OCPD of 800amps. 250.66 states that the GEC should be a 1/0 copper conductor. Can this be connected to ground rod?
The size of the GEC is determined by the ungrounded conductors, not the OC protection size. 3/0 copper run to a 20 amp beaker would require a 4 AWG copper