Ground rod location

Status
Not open for further replies.

mdh

Member
Hello,had a Inspector ask me to move a ground rod for a service because the ground rod would be under the concrete driveway he said it needed water to keep a good earth ground

I have not seen this in the code so if it is there please help

MDH
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
mdh said:
Hello,had a Inspector ask me to move a ground rod for a service because the ground rod would be under the concrete driveway he said it needed water to keep a good earth ground

I have not seen this in the code so if it is there please help

MDH

It is not in the code book. 2 ground rods is all that is required if you cannot get 25 ohms to ground with one.
 

celtic

Senior Member
Location
NJ
Interesting.

In many urban areas, there is no area not covered by concrete driveways/sidewalks.
 

mdh

Member
BTW The water piping is copper so the ground wire also ties with-in 5 feet of the copper water piping system, that water company uses.the poco only requires 1 rod for a 200 amp or less 3 rods for 400 and above anyway I told him to show a code ref to support his want he could not as of friday
 

mdh

Member
hey I also had another Inspector tell another that the ground rod driven under a wooden deck should have been where rain could get to it but he let it go
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
mdh said:
BTW The water piping is copper so the ground wire also ties with-in 5 feet of the copper water piping system, that water company uses.
The water pipe electrode is required to be supplemented by one or more electrodes, so if there are no other electrodes present then a ground rod may be driven to meet this requirement. 250.53(D)(2).

If that ground rod is not 25 ohms to earth or less, then one more ground rod is required - from there, even if the pair of rods exceed 25Ω then no more are required to be driven.

the poco only requires 1 rod for a 200 amp or less 3 rods for 400 and above anyway I told him to show a code ref to support his want he could not as of friday
Well, ground rods are required to be driven below permanent moisture level (250.53(A)), but generally this requirement is largely ignored, IMO - usually, the rod is driven until it is flush, or perhaps an inch above grade for visibility for inspection (or perhaps a misguided belief that the connection must remain accessible). Permanent moisture could be a foot or two below grade.

If the inspector believed no moisture would be present below the driveway, then he would have a case for moving the rod.

However, I believe the earth immediately under that slab of driveway concrete would be below permanent moisture level, I find it hard to envision dry earth under that slab at any time, IMO.

If the foundation of a new building contains a concrete-encased electrode (CEE), then it (and all other electrodes present) must be used (250.50). If you have a CEE connected to the electrical system, then no ground rods are required to be driven, since the CEE is supplementing the water pipe ground. (I say this ignoring your power company's requirements, which are unique to your area, IMO.)

Hope that helps,
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
mdh said:
hey I also had another Inspector tell another that the ground rod driven under a wooden deck should have been where rain could get to it but he let it go
So the earth under a porous deck that never sees sunshine is dry? :roll:

Where are you located, Death Valley?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If you are in the Southeast everything is dry, even ponds and lakes.

Atlanta only has a few weeks of water left.

Roger
 

cadpoint

Senior Member
Location
Durham, NC
Place it here!

Place it here!

mdh said:
Hello,had a Inspector ask me to move a ground rod for a service because the ground rod would be under the concrete driveway he said it needed water to keep a good earth ground

I have not seen this in the code so if it is there please help

MDH

Sure why not it'll, burn off the oxygen to ignite the hydrogen ...
Via a lighting strike ...
 
Last edited:

romeo

Senior Member
Ground rod location

mdh said:
Hello,had a Inspector ask me to move a ground rod for a service because the ground rod would be under the concrete driveway he said it needed water to keep a good earth ground

I have not seen this in the code so if it is there please help

MDH

So much for a ufer ground.Be sure that the grd, clamp is listed for direct burial and be on your way.
 

mdh

Member
My location is in east Tn,Thanks for all replys neither Inspector could quote a code violation both said that is what they would like to see.concrete is over my ground rod and a deck over the other one
 