I just can't be sure whether a ground rod is required at this detached garage or not. Please cite the specific article.
1. Residential detached garage
2. No piping of any kind in the garage
3. Underground feed from house main panel via a 30 amp 2 pole breaker at 120/240 volts
4. Equipment ground and neutral is provided to 4 circuit sub-panel where neutral is isolated from ground
Do I install a ground rod and bond the neutral at the garage and not use the equipment ground in the feeder? Or do I treat this as I would a sub-panel within the house (provide an isolated neutral)?