I have done a 3 point or fall of potential test on ground rods. The one I did was not connected to the service neutral. Just had rods in the earth without the conductor.
Are there tests that test the rods while connected to the service neutral. Imo, that defeats the purpose and it is not testing the rods. I heard one electrician say he uses the entire system to get his 25 ohms. Is that correct?
Are there any tests for ground rod resistance where you are connected to the service neutral? Here is what I did

Are there tests that test the rods while connected to the service neutral. Imo, that defeats the purpose and it is not testing the rods. I heard one electrician say he uses the entire system to get his 25 ohms. Is that correct?
Are there any tests for ground rod resistance where you are connected to the service neutral? Here is what I did