JDBrown
Senior Member
- Location
- California
- Occupation
- Electrical Engineer
I could have sworn I read somewhere that a residential outbuilding (shed, detached garage, workshop, etc.) supplied by a feeder only needs 1 ground rod, but now I can't find it.
I know you can get away with only 1 ground rod if you have another electrode at the structure (rebar in the footings, metal water pipe, etc.), or if you test the resistance to ground < 25 Ohms (NEC 250.56). But it seems like this was an Exception specifically for residential outbuildings, somewhere along the lines of the Exceptions in 225.36 and 225.38 allowing snap switches as a disconnecting means for residential outbuildings.
I've been searching through the NEC, but I can't find it anywhere, so I'm starting to think I must really be remembering things wrong. Does such an Exception even exist?
I know you can get away with only 1 ground rod if you have another electrode at the structure (rebar in the footings, metal water pipe, etc.), or if you test the resistance to ground < 25 Ohms (NEC 250.56). But it seems like this was an Exception specifically for residential outbuildings, somewhere along the lines of the Exceptions in 225.36 and 225.38 allowing snap switches as a disconnecting means for residential outbuildings.
I've been searching through the NEC, but I can't find it anywhere, so I'm starting to think I must really be remembering things wrong. Does such an Exception even exist?