Re: Ground rod testing
American electric, the meters are expensive. Your best bet is to rent one. It is really a tool of inspectors and engineers. I suppose a large EC firm could justify one. I prefer a 3-point tester as it is more accurate. The loop tester measures the ground under test in series with the utility ground through the service neutral. I have seen results where it measured 54 ohms when ground ring and chemical rods were both used. When the 3-point was used, the GES measured 6-ohms. The remaining 48-ohms was the utility ground.
I work in the telecom sector and deal with equipment vendors and IT people on a daily basis. Ground impedance comes up constantly, and in my experience, ground always gets falsely accused. No matter what impedance is measured, it is never low enough to satisfy them. You mentioned this is a car dealership, so there is no practical reason to have a GES with an impedance of 5-ohms or less to satisfy a IT rep.
Here are a few things I would look into:
Is the GES in good repair, and meets code?
Is the N-G bond in the proper location, and no downstream N-G violations?
Are EGC?s run with all feeders and branch circuits?
Is there a Class ?C?, UL-1499 second edition service entrance rated TVSS installed at the service entrance?
Is there a Class ?B?, UL-1499 second edition TVSS installed in branch panels?
Is there a Class ?A?, UL-1499 second edition, point of use TVSS used on sensitive equipment?
Does sensitive equipment use dedicated AC circuits?
Does sensitive equipment use any ground or grounded signal- interconnect cables such as coax, RS-232, or RS-422?
Do they power their sensitive equipment via a dual conversion UPS?