Can i use a 3/4" galvanized pipe 10' long for a ground rod 2011 nec. when did the nec start letting you do this?
When I was a helper, that was all we ever used, driven with a sledge hammer.Can i use a 3/4" galvanized pipe 10' long for a ground rod 2011 nec. when did the nec start letting you do this?
Not EMT.But how do you pound in a 3/4” galvanized EMT with thinner walls as you would a 1/2” rod?
But couldn’t you use emt if you had a hole dug 10 feet?Not EMT.
Back in my day we used RMC. Ridged,GRC.
Then we got 5/8" galvanized rods.
But couldn’t you use emt if you had a hole dug 10 feet?
No, because EMT technically isn't conduit or pipe.But couldn’t you use emt if you had a hole dug 10 feet?
I wanted to add. From UL white book.No, because EMT technically isn't conduit or pipe.
EMT is conduitNo, because EMT technically isn't conduit or pipe.
No it's not, it's tubingEMT is conduit
No, it merely resembles conduit.EMT is conduit
Both covered by same subsection in NEC titled "Rod and pipe electrodes" Which has existed for a very long time.Can i use a 3/4" galvanized pipe 10' long for a ground rod 2011 nec. when did the nec start letting you do this?
That has been permitted by the code for many decades....well before I started in 73.
Not sure if it was ever legal, but dwelling unit services from the 60s and earlier around here not only used 3/4" conduit as the grounding electrode, but used 1/2" conduit as the grounding electrode conductor. They used a "service LB that had a 1/2" tap in the bottom and the 1/2" was run down into the ground, had a 90 on it, and was connected to the 3/4" pipe with a wedge clamp.
I have looked a couple of times for pictures of the wedge clamp without success.
That is how I remember the clamp too. Around here they always used the service LB with the 1/2" tap on the bottom. They were this type but with the 1/2" hub on the bottom for the 1/2" rigid that was used as the grounding electrode conductor. No wire conductor, the larger conduit to the service panel was bonding with a bonding bushing and GEC sized jumper in the service panel.Yes, while in HS I worked Saturdays re-stocking trucks for an electrical outfit. This was in 1965-66.
We used a piece of 1/2 rigid conduit, that went into a 1/2 KO in the bottom RH back corner of the meter base (with a grounding bushing and jumper to the neutral conductor,) then down and thru a 90 bend to the 3/4" ground pipe also rigid conduit 10 ft long...One of my jobs was to make sure that there were always 8-10 pre-made 1/2" pieces in stock, as I recall it took a 6-ft 9-inch length with the bend that would place the 3/4 rod about 1`2 inches from the building foundation and a foot undeground.
And Don, it appears that pictures of that wedge clamp have been purged from existence....I've gone thru old Sears and MW 'farm' catalogs and no trace. It was a U-shaped piece of galvanized steel, the U was sized to fit around the 3/4 pipe, each end of the U had a hole large enough for the 1/2" to fit thru, and then the two wedges were driven into the 'corner' formed by the two pipes.