A acman52 New member Sep 26, 2004 #1 Of the 8 foot ground rod how much is the min. reqiured to be in the ground by code?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Sep 26, 2004 #2 Re: ground rod all of it
B bphgravity Senior Member Location Florida Sep 26, 2004 #3 Re: ground rod See Section 250.53(G) of the NEC 2002.
6 612278 Member Sep 27, 2004 #4 Re: ground rod Hey- And if bury it the connections must be rated as such. (exothermic, clamp etc.) Steve
Re: ground rod Hey- And if bury it the connections must be rated as such. (exothermic, clamp etc.) Steve
electricmanscott Senior Member Location Boston, MA Sep 27, 2004 #5 Re: ground rod Don't forget that if practicable you must install the rod below permanent moisture level. 250.53(A)
Re: ground rod Don't forget that if practicable you must install the rod below permanent moisture level. 250.53(A)