A acman52 New member Sep 26, 2004 #1 Of the 8 foot ground rod how much is the min. reqiured to be in the ground by code?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Sep 26, 2004 #2 Re: ground rod all of it
B bphgravity Senior Member Location Florida Sep 26, 2004 #3 Re: ground rod See Section 250.53(G) of the NEC 2002.
6 612278 Member Sep 27, 2004 #4 Re: ground rod Hey- And if bury it the connections must be rated as such. (exothermic, clamp etc.) Steve
Re: ground rod Hey- And if bury it the connections must be rated as such. (exothermic, clamp etc.) Steve
electricmanscott Senior Member Location Boston, MA Occupation Massachusetts Master Electrician, one man show. Sep 27, 2004 #5 Re: ground rod Don't forget that if practicable you must install the rod below permanent moisture level. 250.53(A)
Re: ground rod Don't forget that if practicable you must install the rod below permanent moisture level. 250.53(A)