Does anyone know when the NEC started requiring a ground rod at a seperate structure? Detached garage with a subpanel and three wire feeder. No EGC run with feeder and no ground rod. Home inspector noted that panel is not grounded and I am looking for a fix.
Don't bother, it predates that by half a century, I think.I am not that old but I think a ground rod or water line ground has all ways been required. I'll get my 1947 NEC book out and look it up![]()
No EGC run with feeder and no ground rod. Home inspector noted that panel is not grounded and I am looking for a fix.
Don't bother, it predates that by half a century, I think.![]()
Bond the neutral to the EGC of the detached structure as allowed in 250.32 and drive the ground rod. Simplest code compliant solution.
The difference is whether the separate building is supplied via a single (incl. 3-wire) circuit that originates from the main building, or whether circuits in the separate building originate from a panel in that building.I have run across quite a few garages without one, and was told it wasn't required back then since the service had an electrode?