If you have a 200 amp panel that goes to a 30 amp sub-panel for a timer for a lagoon would a ground rod be required at both panels. I thought yes, but the electrician thinks not. Who is right?
If you have a 200 amp panel that goes to a 30 amp sub-panel for a timer for a lagoon would a ground rod be required at both panels. I thought yes, but the electrician thinks not. Who is right?
It depends on whether the panel is just one dp breaker or if the panel had more than 2 circuits. If this is simply a 240v circuit and a disconnect out at the lagoon then I say no based on art. 225.30
Even by that description, it's still a seperate structure. So IMO 250.32 (a) applies
I agree it is a separate structure but if it is just a MWBC then there is no need to use 250.32. Look at the except. to 250.32(a).Even by that description, it's still a seperate structure. So IMO 250.32 (a) applies
250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).
(A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.
Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non?current-carrying metal parts of equipment.
Yes, but the exception to 250.32(A) would allow you to omit the grounding electrode at the separate building if the building is supplied by a single branch circuit, which is what Dennis was eluding to.
Chris
I agree it is a separate structure but if it is just a MWBC then there is no need to use 250.32. Look at the except. to 250.32(a).
I agree with Dennis. (1) breaker, no ground rod.
So if I install a non fused disconnect at the structure then then it is a branch circuit. Add the breaker and I must install a ground rod. Hummmm. I think you are correct with the interpretation of code based on the definition of feeder and branch circuit, but it does not make sense. I also don't believe that is the intent of this section. FWIW-- nothing....If there's (ONE) breaker at the fiinal destination,,,,then this is not a branch circuit.
So if I install a non fused disconnect at the structure then then it is a branch circuit. Add the breaker and I must install a ground rod. Hummmm. I think you are correct with the interpretation of code based on the definition of feeder and branch circuit, but it does not make sense. I also don't believe that is the intent of this section. FWIW-- nothing....
Hey it was my error first. :grin:my error... good catch,..
So did you win the bet or he?