Re: ground rods and portable generators
don_resqcapt,
quote:
__________________________________________________
My point is that if there is no metal underground water piping system, it is highly unlikely that the code compliant grounding electrode system would have made any difference in the case you are talking about.
__________________________________________________
Yes I agree with you.
Such a hypothetical construct does not however negate the efficacy of correctly installed ground rod(s).
I was suggesting, in context with the case that I was talking about (which did in fact have the metal underground water pipe system available) that, using at least a couple of ground rods and spacing them at least 8' apart, doing the best you can to obtain an earth ground resistance of 25 ohms or less with them, would have helped some (underline) to reduce (underline) the current across that 12 AWG equipment grounding conductor in that parallel circuit. A desirable difference will always be realized by a correctly installed and code compliant system.
With no metal underground water piping system available, then of course no return path could there be by means of that 12 AWG EGC bonded to the dishwasher frame and it could not have started the fire anyway.
grandpapastu.
don_resqcapt
quote:
__________________________________________________
The impedance of most code compliant grounding electrodes, other than a common metal under ground water piping system, is too high to permit much current flow.
Don __________________________________________________
O.K., yep, exactly and I agree.
In the case I cited however there was a metal underground water piping system that was tied in with the reconstructed grounding electrode system and if such a system as that had been in place along with code compliant (25 ohms or less resistance to ground) ground rod(s) installed prior to the trouble with the underground service lateral neutral then the current realized across the 12 AWG EGC would have been limited to a negligible value and such value would have been reduced due at least in some part by the code compliant ground rod(s) installed. Any reduction in the value of the current realized across the 12 AWG EGC would have been desirable.
grandpapastu.
[ June 04, 2004, 11:42 AM: Message edited by: grandpapastu ]