Are ground rods required at a separate building which is fed by a two pole breaker at a building near by? The new separate building is being fed by two ungrounded conductors, grounded conductor, and equipment grounding conductor. This goes into a small two space panel/disconnect. From there the two individual breakers feed lights and receptacles.
2020 NEC 250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuits(s)
Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non-current-carrying metal parts of equipment.
After reading this exception, my point of view says that a ground rod would not be required. Any input is appreciated!
Thank you
2020 NEC 250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuits(s)
Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non-current-carrying metal parts of equipment.
After reading this exception, my point of view says that a ground rod would not be required. Any input is appreciated!