A job I'm working on currently takes into account the new NEC code changes involving concrete encased electrodes found in 250.52(A)(3) (This also seems to affect NFPA780 for Lighting Protection as well). As stated in 250.52(A)(2), you can connect the structural metal frame to reinforcing bars of a concrete encased electrode as provided in the section just stated. In the design, we have for the foundation of the building, a drilled shaft that extends at times as low as 30'. Within this structure are vertical bars equally spaced with standard anchor bolts and a cap laid on top at grade, where the steel structure is then connected. More of these structures are then built, some within 20 ft. of each other.
One of the questions I have is can this structure, if connected with an already constructed ground grid, be used in place of a standard ground rod? If so, isnt it well maintained in the industry that the minimum distance between ground rods is 2 times the length of the ground rod itself, or is that an arbitrary sentiment? I know that this design helps improve the contact resistance with the earth. Is it necesarilly bad if they're closer?
Also referencing 250.52(A)(3), what constitutes 20ft of metal rods? The length that it extends from top to bottom of the concrete?, or what if the concrete extends only 5 ft and metal rod is twisted throughout the concrete, eventually obtaining 20 ft of total length?
A long drawn out question, I know. Any help is appreciated.
One of the questions I have is can this structure, if connected with an already constructed ground grid, be used in place of a standard ground rod? If so, isnt it well maintained in the industry that the minimum distance between ground rods is 2 times the length of the ground rod itself, or is that an arbitrary sentiment? I know that this design helps improve the contact resistance with the earth. Is it necesarilly bad if they're closer?
Also referencing 250.52(A)(3), what constitutes 20ft of metal rods? The length that it extends from top to bottom of the concrete?, or what if the concrete extends only 5 ft and metal rod is twisted throughout the concrete, eventually obtaining 20 ft of total length?
A long drawn out question, I know. Any help is appreciated.