Attached sketch two scenarios all following the NEC 2014 Article 250.64(D)(1),(2) or (3).
Scenario #2 shows tapped grounding electrode conductor (GEC) label #2 from each service disconnect to ground busbar. From the ground busbar their is common grounding electrode conductor label #2 go to ground rods per NEC 2014 Artocle 250.64(D)(3). Between ground rod their is also conductor #1 connecting the rods as shown in sketch.
Scenario #1 their is GEC labeled #2 from neutral bar in service trough to building steel and from steel their is bonding jumper to ground rods. Between ground rod their is also conductor #1 connecting the rods as shown in sketch.
Following questions:
1. Scenario #2 conductors #2 and #1 common grounding electrode conductor which code section would determine their size? #6 Awg is ok or size per Table 250.66 greater than #6 awg?
2. Scenario #1 conductors #2 and #1 bonding jumper which code section would determine their size? #6 Awg or size per Table 250.66 greater than #6 awg?
3. If the ground busbar is in the service trough would that be considered accessible per NEC 2014 Article 250.64(D)(1) or it would not be consider accessible?
Please all reference NEC 2014
Scenario #2 shows tapped grounding electrode conductor (GEC) label #2 from each service disconnect to ground busbar. From the ground busbar their is common grounding electrode conductor label #2 go to ground rods per NEC 2014 Artocle 250.64(D)(3). Between ground rod their is also conductor #1 connecting the rods as shown in sketch.
Scenario #1 their is GEC labeled #2 from neutral bar in service trough to building steel and from steel their is bonding jumper to ground rods. Between ground rod their is also conductor #1 connecting the rods as shown in sketch.
Following questions:
1. Scenario #2 conductors #2 and #1 common grounding electrode conductor which code section would determine their size? #6 Awg is ok or size per Table 250.66 greater than #6 awg?
2. Scenario #1 conductors #2 and #1 bonding jumper which code section would determine their size? #6 Awg or size per Table 250.66 greater than #6 awg?
3. If the ground busbar is in the service trough would that be considered accessible per NEC 2014 Article 250.64(D)(1) or it would not be consider accessible?
Please all reference NEC 2014