Hope that I can get some help. We have been having a huge discussion about Parallel paths to ground. The issue came about on an installation that I had not seen before, but have found nothing in the code book to say that it is incorrect. So, the issue is:
Generator is bonded neutral to ground
Electrical panel inside of the building is not bonded neutral to ground
There are 5 conductors running from generator to electrical panel (3 phases, 1 neutral, 1 ground)
A ground rod is driven into the ground at the generator
A ground rod is driven into the ground at the building
A conductor is run from the ground lug of the generator to the first ground rod to the second ground rod and then to the bus bar of the electrical panel inside of the building unbroken
By running the GEC from the generator to the ground rods and to the electrical panel inside of the building does this create a parallel path to ground? Our company policies require that a ground rod is driven at the generator and at the electrical panel. Would this setup be suitable for a 4 conductor system from the generator to the electrical panel?
Generator is bonded neutral to ground
Electrical panel inside of the building is not bonded neutral to ground
There are 5 conductors running from generator to electrical panel (3 phases, 1 neutral, 1 ground)
A ground rod is driven into the ground at the generator
A ground rod is driven into the ground at the building
A conductor is run from the ground lug of the generator to the first ground rod to the second ground rod and then to the bus bar of the electrical panel inside of the building unbroken
By running the GEC from the generator to the ground rods and to the electrical panel inside of the building does this create a parallel path to ground? Our company policies require that a ground rod is driven at the generator and at the electrical panel. Would this setup be suitable for a 4 conductor system from the generator to the electrical panel?