Ground Rods In Basement Mechanical Room

Status
Not open for further replies.

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
Drilling through the basement floor and driving the rods down into the earth. I've done this before when freezing temps and snow are present. Just wondering if anyone else has thoughts on this method?
 
and the rods are longer than 8', correct?

One of my competitors drove one right through the sewer line. He lucked, the intents were to move that line in the future anyway. (commercial project)
No....they are 8' long. I drill a 1 1/4" hole in the concrete to allow for the acorn and drive the rod down so the entire length is in contact with the earth.
 
Ground rods are required to have 8ft in contact with soil. If the clamp is exposed it must be protected , see 250.10 or so
 
I have read it before many years ago, but it may have been in the explanation part of the handbooks.
Explanatory material in the handbook is not official NFPA interpretations it is simply opinion of whoever authored it. Mike Holt's books, videos, live presentations are no different, any explanations he makes is his ideas/opinions and not any kind of official NFPA interpretation either. People that present such kinds of information often have a fair amount of credibility to back them up may even be able to quote CMP comments, reports, etc. to help back up some of what they say, still are not official representation of NFPA though.
 
Explanatory material in the handbook is not official NFPA interpretations it is simply opinion of whoever authored it. Mike Holt's books, videos, live presentations are no different, any explanations he makes is his ideas/opinions and not any kind of official NFPA interpretation either. People that present such kinds of information often have a fair amount of credibility to back them up may even be able to quote CMP comments, reports, etc. to help back up some of what they say, still are not official representation of NFPA though.
Exactly. Just know I have seen it. Generally NFPA does not explain why they do anything! LOL!
 
That’s why I always buy the handbook.
PI's (public inputs) are not specifically mentioned in handbook. You need to go to NFPA website and look at the draft reports for a particular year, you will see all public inputs (formerly known as proposals) and the CMP decisions, with reasons if they rejected a PI. This is probably closest you get to NPFA interpretation without actually trying to request one, but for code language that been in existence for some time you have to find the right year when it changed to see the information on why it changed.
 