Electricjunky
New member
- Location
- Arkansas
Ok, I'm on a spec job with primarily clean rock. 1st ground registered 944 ohms. I then ran a 2nd over to the fence line, so I could try to catch a little dirt. It lowered my ohms to 48. I then moved 20' further along the fence line, and drove another rod. That lowered my ohms to 14.85. Out of curiosity, I removed the 1st ground rod from the series, since it registered 944 ohms. My ohms on the remaining two then dropped slightly to 14.05 ohms. Why is this? Is there a threshold where ground rods in high impedence soil give no benefit to a series of ground rods? Same thing happened on a separate site across town. Removed 2 ground rods that registered 600 ohms independently, from a series of 6 ground rods. The remaining 4 had the the ohms, as it was with 6 ground rods. Is their a resource that I can refer to to better understand why that is. Thanks.