Ground rods on generators

Status
Not open for further replies.
We are trying to stay compliant with NEC. We use 70-125 KW generators to supply our trailers houses on land rigs. Does our generators need to be grounded with ground rods? Was told generators may not need to be grounded according to 2014 NEC codes.
 
harpo

harpo

We are trying to stay compliant with NEC. We use 70-125 KW generators to supply our trailers houses on land rigs. Does our generators need to be grounded with ground rods? Was told generators may not need to be grounded according to 2014 NEC codes.

if it is a separately derived system, yes. if it is a non s.d.s. system, no.
 
If the generator is a SDS, then you need a grounding electrode system and a system bonding jumper. There are also new sign requirements in Art 702.
No changes in the 2014 NEC on grounding for generators for what you are doing
 