treyp3
Member
- Location
- Fernandina Beach Fl
My inspector is telling me I'll need ground rods on a sub panel in a detached garage. I want to run a four wire feeder to the sub panel. 250.32(B)(1) states -
"an equipment grounding conductor shall be run with the supply conductors and connected to the building or structure disconnecting means and to the grounding electrodes"
So, shouldn't the subpanel in the detached garage be tied in back at the GEC in one location only back at the point of service?
Code source please
"an equipment grounding conductor shall be run with the supply conductors and connected to the building or structure disconnecting means and to the grounding electrodes"
So, shouldn't the subpanel in the detached garage be tied in back at the GEC in one location only back at the point of service?
Code source please