Re: ground rods
In some areas the general experience is that the soil is so poor that they just flat require 2 rods if you are using them. Some areas that flat require 2 rods if you are using them:
1. West Penn Power in PA
2. New York State
3. Geauga County, Ohio
Actually, New York State requires that you also use #4 solid copper to hook up the ground wires. It must run unbroken from the service ground bus to the first rod, loop unspliced through the clamp and then to the second rod, run unspliced through the second rod clamp, and then back to the service using a different physical path. Any trench or protective conduit cannot be shared by the 2 segments that are connected to the ground bus in the service switch. This is so that if the GEC is ever cut, you still have 2 rods.
The mechanical protection requirement in NEC 250.64(B) can also dictate that the GEC for a ground rod be #4 copper. Some places such as Akron, Ohio do not allow a GEC smaller than #4 solid or #2 stranded copper because they do not want to take time to determine if #6 copper is protected enough. The #6 copper wire rule for a plate or rod electrode is 150 year old rule from when telegraph systems were wired with #6 steel wire.