ground rods

Status
Not open for further replies.

GG

Senior Member
Location
Ft.Worth, T.X.
Re: ground rods

Zero if you have a cold water ground and go to the rebar in the footing.

[ July 17, 2005, 11:32 PM: Message edited by: GG ]
 

macmikeman

Senior Member
Re: ground rods

Not exactly, what it does require is that if you are using ground rod as a supplemental electrode it must present no more than 25 ohms of resistance which is not so easy to prove. You would need to perform a ground rod test to show it does not have a higher resistance. So therefore it is usually much easier to just get the second rod in and be done with it. See 250.56 for reference. P.S. Inspectors where I am at have never asked me for rod #2 yet, except for in cases where the plumbers used plastic wrap over the buried copper water pipes.
 

GG

Senior Member
Location
Ft.Worth, T.X.
Re: ground rods

No problem macmikeman. Where I live the utility wont put a meter in unless they see a ground rod anyway so your post would be the norm here. Plus like you I haven't had an inspector have me drive a 2nd rod or show proof of 25 ohms.
 

allenwayne

Senior Member
Re: ground rods

It amazes me how in different areas different requirements are used.Here we work in 4 different jurisdictions.But have four different requirements.
Area 1-just a footer bond unless water is CU then it has to be used also.
Area 2-2 ground rods and water if CU.
Area 3-1 ground rod with a footer bond and water if CU.
Area 4-has just started using footer bonds.but for the slabs poured before the required uffer we had to chip into a poured up lift cell find rebar attach to it and then hit 2 ground rods and water if CU,I never understood having to chip into an uplift cell in a block wall since that piece is only about 6 ft long and tied to 20 ft of rebar that is in the slab.
Our biggest problem has been theft of copper when slabs have been poured,usually they leave a piece that is around a foot long :p
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Re: ground rods

Gosh! Such confusion. You would think someone would come up with a national Code :)
 

romeo

Senior Member
Re: ground rods

If underground water pipe is used as the grounding electrode system it must have a supplemental electrode 250.53(D)(2). I believe the reason is that if the underground water pipe is ever replaced it will be changed to plastic. So it is important that if a ground rod is used to supplement
the water pipe it must meet the 25 ohm requirement or a second ground rod must be used, and it must be at least 6ft. from the first.
Inspectors that are allowing 1 ground rod are not doing there job, and should have a hard time sleeping at night. romeo
 

charlie

Senior Member
Location
Indianapolis
Re: ground rods

Inspectors that are allowing 1 ground rod are not doing there job, and should have a hard time sleeping at night.
I can't agree with that statement. It depends on the area's soil conditions. If it is normal to get 15 &#8486 in a subdivision and homes are going in the same area, why require two rods? Some people do measure their ground resistance. :D
 

mc5w

Senior Member
Re: ground rods

In some areas the general experience is that the soil is so poor that they just flat require 2 rods if you are using them. Some areas that flat require 2 rods if you are using them:

1. West Penn Power in PA
2. New York State
3. Geauga County, Ohio

Actually, New York State requires that you also use #4 solid copper to hook up the ground wires. It must run unbroken from the service ground bus to the first rod, loop unspliced through the clamp and then to the second rod, run unspliced through the second rod clamp, and then back to the service using a different physical path. Any trench or protective conduit cannot be shared by the 2 segments that are connected to the ground bus in the service switch. This is so that if the GEC is ever cut, you still have 2 rods.

The mechanical protection requirement in NEC 250.64(B) can also dictate that the GEC for a ground rod be #4 copper. Some places such as Akron, Ohio do not allow a GEC smaller than #4 solid or #2 stranded copper because they do not want to take time to determine if #6 copper is protected enough. The #6 copper wire rule for a plate or rod electrode is 150 year old rule from when telegraph systems were wired with #6 steel wire.
 

romeo

Senior Member
Re: ground rods

Charlie Maybe I was not clear. I said that a second ground rod should be used only if the first one did not meet the 25 ohm requirement.

romeo
 

romeo

Senior Member
Re: ground rods

Ryan That is your choice and I respect that. I just worry that a metal underground water pipe could be changed to plastic and there would be no grounding electrode system left.

romeo
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: ground rods

Romeo, worrying about what may happen in the future is not a justification for requiring over and above what your adopted codes are.

What would you do if there is a piece of equipment calling for a 125 amp fused protection, it is fed with 125 amp conductors and protected with 125 amp fuses in a 200 amp fusible switch, would you require this be changed somehow due to the fact that some time in the future someone may put larger fuses in?

We simply can not control the "What Ifs"

On another note, even if these rods combined got down to 5 ohms total resistance they aren't doing much anyways, I call them placebos.

Roger

[ July 19, 2005, 07:42 AM: Message edited by: roger ]
 

romeo

Senior Member
Re: ground rods

Roger Supplemental electrodes for a underground metal water pipes is not over and above NEC requirements it is required by section 250.53(C)(2). Also I would not require a change for the 125A. circuit you mention because it is not a violation.

romeo

P.S. I am not trying to start an issue here just gave IMO . Thanks
 

ryan_618

Senior Member
Re: ground rods

I just don't get that excited about ground resistance.

Ya know, it's funny. The main function of the grounding electrode system is for lightning protection. The NFPA 780 (lightning protection) says to drive two 10 foot ground rods and call it a day. Why do we have to have ufer's and water pipes and building steel and ground rods and everything else? :confused:
 