jaggedben
- Northern California
- Solar and Energy Storage Installer
You need full-sized conductor between main disco and water pipe, only #6 cu between main and rods or between water pipe and rods.
I don't agree that's clear. Main GEC to the grounding electrode system is sized per 250.66. I think if it connects both rods, that's its size. Bonding jumper from the first to the second rod is not required to be more than #6. If you run separate GECs or bonding jumpers to each rod they are not required to be more than #6.