timmermeier
Member
- Location
- alton il
- Occupation
- electrician
A 1/2" ground rod must be UL listed, but a 5/8" ground rod does not need to be UL listed ??????????????????????????????????????????????????
250.52.5 BA 1/2" ground rod must be UL listed, but a 5/8" ground rod does not need to be UL listed ??????????????????????????????????????????????????
Yes. You could also use an 8' length of 3/4" or larger RMC as the electrode which isn't listed as a ground rod either.A 1/2" ground rod must be UL listed, but a 5/8" ground rod does not need to be UL listed ?
250.52.5 B
3/4" RMC MUST BE 10 ' .Yes. You could also use an 8' length of 3/4" or larger RMC as the electrode which isn't listed as a ground rod either.
Do you have a code section?3/4" RMC MUST BE 10 ' .
NO IT IS 8' MY BAD !Do you have a code section?