Re: ground rods
Ground rods may provide and effective fault current path
Hello,
I have a subject of interest that I would like to address please. Pertaining to Mike Holt's Video & Graphics site: 'Ground Rod Does Not Provide Any Protection From Electric Shock (2 of 2), the statement made under this site: ?Electrons do not take path of least resistance and a ground rod does not provide an effective fault current path,? is questionable to me.
Does this statement imply that it is believed that some understand electric current to take the path of least resistance only and therefore leave them unaffected if they get into the circuit?
(1) If this were true, then why does a 100 watt light bulb draw more current (but not the only current) than a 60 watt light bulb when it is connected in parallel with the 60 watt light bulb in a 120 volt two-wire single-phase circuit?
(2) Why then, in a parallel circuit:
Et=E1=E2=E3=En
It=I1+I2+I3+In
Rt=1/(1/R1+1/R2)
Electric current (the flow of electrons) generated by an electromotive force seeks the path of least resistance to ground, not the path of least resistance only. In fact, electric current seeks any conductive path to ground that may turn out to be a designed or accidental parallel, series, or parallel-series path of electron flow.
A dishwasher homerun circuit at an emergency residential service call, Peachtree City, GA assigned to me started an attic fire.
A very high impedance - nearly open - public utility provided underground service lateral grounded conductor (R3) caused system operating current to seek a ground return path by means of and through the 12 AWG equipment grounding conductor of the 20A dishwasher branch circuit homerun (R2) from the 150A 120/240volt main breaker panel ground buss to the bonded frame of the dishwasher and it's connected copper plumbing to earth ground.
A single ground rod and it?s GEC (R1) tapped to the service grounded conductor at the meter base-service point was the systems only grounding electrode.
The metal plumbing of the house was not bonded as part of the grounding electrode system.
The three wire SEU service entrance grounded conductor connected from the MBO panel to the grounding electrode (R1) at the service point, and the dishwasher circuit equipment grounding conductor from the MBO panel to the underground water plumbing (R2) formed a parallel path for current flow to ground that was in series with the service lateral grounded conductor (R3).
(4) In this case could not two ground rods (R1) driven with 8' earth contact driven no less than 8' apart provide significantly lower impedance to ground than the single existing ground rod which was driven more than 20' away from the service point? Without a doubt the existing grounding electrode was also providing only a very high impedance to ground, as they usually will in time, because of changing soil conditions, ground rod corrosion, oxidation of GEC connections, etc.
(5) With a low impedance path provided by a repaired service lateral grounded conductor (R3) back to the transformer pad, would not the majority of the system operating current be on that conductor and any other current reduced to zero or a negligible value? E/R=I
(6) Bonding the water pipes correctly from the service point with a correctly sized GEC would have reduced the current that was present over the dishwasher circuit equipment grounding conductor and connected plumbing to a smaller value right?
Concerning your Video & Graphics site here considered that pictures a man getting shocked by an energized light pole, I calculated that he would realize about 80mA across his heart. The 80mA would be sufficient to prove fatal. If a ground rod were not used to ground the light pole, then the man would have been the only available path to ground and the current felt across his heart would have been much greater increasing the probability of death.
Stuart.