Ground rods

Merry Christmas
Status
Not open for further replies.

bwyllie

Senior Member
Location
MA
I am interested in people's opinion on installing ground rods in addition to bonding the water meter and building steel to form the grounding electrode system.
 

ryan_618

Senior Member
Re: Ground rods

My opinion is that its not required in the application you spelled out. If you decide you want to drive one, you have to use it. Doesn't matter to me though.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: Ground rods

I disagree.

What about the requirement for a supplemental ground rod?

If you are "bonding" the water meter(?), to what are you bonding it?

Mike P.
 

thomasf

Member
Re: Ground rods

I agree with Mike, if you have a water meter to ground/Bond it implies you have a water line, and if you have a water line it must be used as a grounding electrode, then accordingly it must be supplemented by a ground rod(s).
However, if the water line to the house is plastic then you would bond the interior water lines if metal, but what would be the purpose of bonding the meter if one side is plastic?
we usually use ground rods if there is no water line or if plastic and bond the interior water lines if metal.

Tom

[ July 29, 2003, 08:06 PM: Message edited by: thomasf ]
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Ground rods

Mike P, maybe I am wrong, but as I read 250.53(D)(2) a water pipe shall be supplemented by an additional electrode specified in 250.52(A)(2) through (A)(7).

The condition describes a water pipe and building steel. The building steel supplements the water pipe (250.52(A)(2)).

Do I mis-understand your post?
 

bennie

Esteemed Member
Re: Ground rods

Unless there is a ground resistance test, the building steel can not be assumed to be a ground electrode. (Effectively Grounded Article 100.)
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Ground rods

Mike I understand where you are going with this. If the building steel is effectively grounded, then yes it is an electrode IMHO.
 

eprice

Senior Member
Location
Utah
Re: Ground rods

If the building steel is effectively grounded, then I agree with what Dereck and Ryan have said. But if the only grounding electrodes are a metal water line (which must be supplemented) and building steel, I would want to look closely at the building steel to make sure that it really is effectively grounded so that it can be considered an electrode.

I haven't been faced with this situation, since around here a Ufer ground is typically also provided. So I am curious, What would make the rest of you feel comfortable with considering the building steel at a particular installation as being effectively grounded? The definition in article 100 seems to imply more than just casual acceptance. Bennie has suggested a resistance test.

[ July 31, 2003, 05:04 PM: Message edited by: eprice ]
 