Re: ground rods
Here in Georgia, we're now required to install two (2) 5/8" X 8' ground rods, spaced 6' apart-on all services
*******************
Either you have local amendments to the NEC or the AHJ is overreaching his bounds.
********************
Well, maybe not. The way I read 250.56, is if you need to have a ground rod, the resistance to ground shall be 25 ohms or less or you drive another ground rod. Once you drive the second ground rod, there is no requirement for resistance to ground.
Where I live, I can guarantee the ground resistance of a properly installed rod will be 100 to 2000 ohms depending on the time of year.
For residential, the AHJ (generally the local utility) recognizes the rod is essentially useless anyway, and generally require just one rod. And they don't require any ground resistnce measurement. The local utility doesn't have any NEC amendments - I don't think they even have the authority of law. They are no going to connect your power unless the service looks like the picture they have.
But for industrial, for a isolated structure, where building steel is not available, I have the electricians drive two ground rods. I have never bothered to measure any of them. No use to. Meets code and is certainly no more useless that one ;-) Which turned out to be a good idea, cause our very own inspector got a new clamp-on ground resistance tester ;-)
So, it could be the ground conditions in the area are known to have poor resistivity, the local utility (AHJ) wants to follow the code, and is just having two rods installed.
carl