What size wire do you run to ground rods if you have an hundred amp service. I ask this because I ran #8 and fail inspection, should it have been #6
 
It depends on the size of your service entrance conductors. Look at 250.66 and remember the gec never needs to be larger than #6.
 
It could also be a damage protection thing. A #8 GEC has to be in a conduit. A #6 can be exposed if closely following the surface of something.

A 100A residential service would normally only need a #8 copper GEC. But as Dennis said, it depends on the size of your service conductors.
 
Never say never. The #6 max rule only applies to rod plate and pipe electrodes.
The title of the thread is ground rods....I thought that was what we were talking about. And yes if you use the rod as a bonding jumper to a water pipe or another electrode than it may need to be larger than #6. I'll say almost never....and I have never used an electrode larger than #6 to the thousands of rods I installed. :p
 
The title of the thread is ground rods....I thought that was what we were talking about. And yes if you use the rod as a bonding jumper to a water pipe or another electrode than it may need to be larger than #6. I'll say almost never....and I have never used an electrode larger than #6 to the thousands of rods I installed. :p

Just for clarification you said the gec never needs to be larger than #6.

Better wording would maybe be ..the conductor that is the sole connection to a ground rod...




Physical protection requirement is different for 8 AWG.

jm1470, what did inspector cite you for? If he can't give you a code section that has been violated I would refuse to change it if I know it is acceptable.
 
I always use #6 for every service between 100-400 amps. Never done one bigger or smaller, so I don't know what I would do in either of those situations.
 
The problem with using #8 to a ground rod is that it must be protected by use of conduit or cable armor. In my area the #6 is allowed unprotected if it is securely fastened to the structure.
 
Yes, the #8 is the minimum size required but must be protected from physical damage by a means outlined in 250.64(B). We just use #6 Cu for every size service to the rods.
 