Look at 250.66 and remember the gec never needs to be larger than #6.
The title of the thread is ground rods....I thought that was what we were talking about. And yes if you use the rod as a bonding jumper to a water pipe or another electrode than it may need to be larger than #6. I'll say almost never....and I have never used an electrode larger than #6 to the thousands of rods I installed.Never say never. The #6 max rule only applies to rod plate and pipe electrodes.
The title of the thread is ground rods....I thought that was what we were talking about. And yes if you use the rod as a bonding jumper to a water pipe or another electrode than it may need to be larger than #6. I'll say almost never....and I have never used an electrode larger than #6 to the thousands of rods I installed.
I always use #6 for every service between 100-400 amps. Never done one bigger or smaller, so I don't know what I would do in either of those situations.
We just use #6 Cu for every size service to the rods.