ground screws
wyboy
Do typical ground screws, the green 10-32?s, have any manufactures installation requirements regarding attaching the ground wire- if it is stranded or solid and direction of twist around conductor and the size (AWG) allowed to be attached. Can?t find much on copper wire in the code.
While you can usually look and see that it's been done right or right enough to pass, I did have one on Thursday where they tried to put a stranded #6 under one and it probably had less than have of the conductor making contact. They put in a lug.
Good point. It is even hard to find information about rated wire and terminal lugs on devices such as breakers. There is nothing in the instruction box or on the devices except the wire sizethat is allowed and the torque requirements. As such it leaves the application open for abuse by using welders cable hypalon, etc unless the NEC is followed in art 310.
But this is for "current carrying conductors" which testing includes tmperature rise and pull tests with the termination tightened to a specified torque.
Since an EGC is not a current carrying conductor the the testing per UL486 does not apply to my knowledge. Remember you are even allowed to place multiple EGCs is a ground bar.
As such is appears as though common sense is what should be used to secure the EGC.