I came by a 480volt service with the only ground connection was to a water line 15-20 feet after entering the building in basement and water meter was on first floor. There also looks like there was at onetime a bare ground connected to the waterline in basement to outside to maybe a ground rod that is now disconnected, not sure , cable is coming into building from outside below ground.
The poco replaced their transformer they labeled 3 phase delta, one phase is grounded [ 0 volts to ground ] and I believe it is a corner ground same as old trans connection. If this is a corner ground 480v connection should the one phase be non protected , and should there be 2 pole breakers instead ? Should the ground system be brought up to date ? Thank you to all help.
The poco replaced their transformer they labeled 3 phase delta, one phase is grounded [ 0 volts to ground ] and I believe it is a corner ground same as old trans connection. If this is a corner ground 480v connection should the one phase be non protected , and should there be 2 pole breakers instead ? Should the ground system be brought up to date ? Thank you to all help.