four said:j-Box in hot tub states Equipment ground should be same size as hots. I dont have any more info (manual). Does anyone know does this mean the same size from tub to tub disconnect (GFI) or from tub to main panel??? 6-3 Romex ground is smaller.
No, it's an NEC issue. See 110.3. Yet, I've never heard of such a thing for Hot T installs. Heck, take a picture of the label, and send it over.four said:Yes your correct. I fugured it was a UL listing issue. I already about got this wired up and then noticed sticker on j-box cover. Didnt know if I missed others in past or if this was something different. Personally I would think it was to GFI breaker because you could have that in a subpanel and feeder to main panel would be different size wire.
Dennis Alwon said:Many Hot tubs require the same size conductor for the ground as the ungrounded conductors. You must install it that way back to the panel to comply with the manufacturers install instructions
Cow said:If that's the case, how would you comply using Romex?
Dennis Alwon said:Well you wouldn't be able to comply if the manufacturer called for a ground equal to the ungrounded conductors. You would have to use a method other than romex. I think it is bull but I have seen this written a few times now.
stickboy1375 said:I know what I would do, but since this is a code worthy site I wont tell you.
infinity said:Install a subpanel maybe?
Bob, I didn't tell him to say that!infinity said:Install a subpanel maybe?
stickboy1375 said:That would be my 2nd choice.
infinity said:Ok, and your first choice?