The prints call for 4 sets of 3/C 500kcmil with a #4/0Gnd to feed a 1600A MCC.
Talking with cable manufacturers, #2 gnd cable is standard and #4/0 is a special order. Can I specify #2 gnd and still be compliant with code?
What size is the OCPD on the supply end of the 4 sets of 500kcmil? 1600 would not be permitted by the code rules.
In that case the EGC only needs to be 3/0 per the code. That is assuming the breaker complies with the rules in 240.6(C).MCC is being fed with a 1600A breaker, dialed down .95...1520A.
500kcmil good for 380A (the one I am going to purchase)...380x4=1520A.
Bob,Don
Table 250.122 allows 3/0 if the breaker setting is not greater than 1200 amps.